Would check my numbers? I have a 10HP air compressor (208v ? 3phase) that I need to hook-up.
It is 10HP
208 3phase
Service Factor 1.15
My calculated load is:
10HP 30.8 Amps
60 Amp Fusible Disc.
60 Amp Time Delay Fuse
80 Amp Circuit Breaker
3#8 THHN/THWN & 1#10 GRD. In 3/4? Conduit
Can I go lower on the Fuse and/or the breaker for the feed?