I have an air compressor to wire that is an air compressor motor, dryer and fan motor in a single unit. It came from Belgium with a motor that is "Inverter duty", and the nameplate says 156 amps at 460 volt. The schematic shows 160 amp as maximum fuse size. There is no nameplate for minimum circuit amps.
Is the wiring for this treated as you would for an air conditioner or motor, where you size the conductors on the 156 amps but upsize the OCP for inrush? (By the way, it has a soft start VSD) Is there NEC reference for these type of "packaged units"?
Also if there is a 300 amp breaker available to feed this, and we put a 200 amp disc. fused at 150 amp, can the entire branch circuit be rated 156 amp? Then the 300 amp breaker is only for disconnecting, short circuit and fault while the 150 amp fuses protect the conductors and package unit?
Thanks for any advise anyone may have...
Is the wiring for this treated as you would for an air conditioner or motor, where you size the conductors on the 156 amps but upsize the OCP for inrush? (By the way, it has a soft start VSD) Is there NEC reference for these type of "packaged units"?
Also if there is a 300 amp breaker available to feed this, and we put a 200 amp disc. fused at 150 amp, can the entire branch circuit be rated 156 amp? Then the 300 amp breaker is only for disconnecting, short circuit and fault while the 150 amp fuses protect the conductors and package unit?
Thanks for any advise anyone may have...