Do motor sizing rules apply to air compressors? I want to say they do, but don't remember off the top of my head.
I'd say generally, yes.
Some of the smaller ones actually have "spl" motors where nameplate data must be used.
It's still Art 430, but an exception.
IMO, I believe the smaller cord & plug type compressors are actually listed (UL) as "appliances" (QDFT) and would be governed by Art 422 and 210 Part II as far as plugs and receptacles.
Other than those, if you cord and plug connected a larger, non-appliance compressor, the cord and plug would need to be HP rated.
It also stated it required a 30A breaker.From the accompanying data it appears to be a 3.7 HP motor at about 14A on 240.
An accessory shows as a 20amp 240v cord & plug.
It also stated it required a 30A breaker.
I just hooked one up this week.
From the accompanying data it appears to be a 3.7 HP motor at about 14A on 240.
An accessory shows as a 20amp 240v cord & plug.
Why not #12 conductor?
125% of the 17.2 = 21.5Amps
and
Because I am following the instructions where relevant and where they are silent I go to NEC. So the instructions don't specify OCPD size so I used the 250%.
The instructions specify a 30A breaker:
“Please consult your local codes and a certified electrician before wiring this compressor for power. (This unit requires a 30 amp double pole breaker for proper installation)”
125% of the 17.2 = 21.5Amps
and
Because I am following the instructions where relevant and where they are silent I go to NEC. So the instructions don't specify OCPD size so I used the 250%.
You are correct - no OCPD rating specified there. I was quoting the website, not the official instructions. Sorry if it caused confusion.