I usually use the max breaker size and size the wire based on that. The customer Has a 45 amp breaker with 10 awg wire. It’s hard to read but it looks like the minimum ampacity and fla of the equipment contradict each other. Would the minimum circuit ampacity supersede the fla based on the unit isn’t running at full capacity? If so would it just be a breaker change for the 10 awg wire?
MCA is the result of 1.25 x compressor rated amps plus the condenser fan motor. I come up with figure very close to what it has, might be there is one more digit on the fan motor that isn't readable anymore that is throwing my result off just a little.
As far as the 10 AWG wire goes on the 45 amp breaker that is acceptable in this situation. The general rules of 240 don't apply, table 240.3 sends you to art 440 for overcurrent protection rules here.
With both art 430 and 440 applications you get higher OCPD for the branch circuit device than for other general applications in 240. They need this high short circuit/ground fault trip level to be able to hold during starting. The normally required separate motor overload protection device protects the motor as well as the conductor from overloads.