Will Wire
Senior Member
- Location
- California: NEC 2020
- Occupation
- Electrical Contractor
In sizing the circuit and protection for the Air Conditioner with the provided nameplate. If I am using 12-2 NMB because of the minimum circuit ampacity of 18.0 amps, does NEC section 240(D) referencing section 240.4(G) allow me to install a 30 amp breaker for Short Circuit, Ground Fault Protection, while section 334.80 states the ampacity of NMB is restricted the 60o C column of Table 310.16?