I have a situation between myself (AC Contractor) and the fire alarm contractor. Here is the story. I have a 10 Ton split system with addressible duct mounted smoke detectors in both the supply and return duct work. The FA contractor has these pan relays that are used to break our 24v control circuit to kill the tstat and ultimately stop the air handler upon a signal from the system. Th ey are saying that my low voltage is burning up the relays. Our low voltage is fed from a 120/24 75VA transformer and I am told the pan relays are good for 3 amps. Our actual primary voltage is about 212v and secondary side is ~26v. Am I crazy or is this not possible. I cannot see that we can b drawing in excess of 3 amps, not to mention, the digital programmable thermostats probable cannot handle 3 amps. Any suggestions?