acguy
acguy
1. Make sure your control system is working within specified parameters.(you probably already know this from start-up)
2. Check the voltage and amperage(I doubt you'll read anything remotely close to 3amps) on the secondary of the control xfmr under full load.(stage 1 cool+stage 2 cool+evap fan+cond fan+etc.)
3. Provide the electrical characteristics of the control circuit(75va @24V) and your readings to the FA contractor. Unless their is some other contractual arrangement or your control circuit is actually malfunctioning, you have done due diligence and the ball is now in the FA contractors court. They need to adapt to the prevailing conditions. Unless you choose to do so, don't put any more of your time and material into this. I would probably get involved out of curiosity or the distinct possibility that I may be wrong.
Some other thoughts:
If there is, in fact, some type of intermittent ground fault/spike, I would suspect that it would be made apparent by a blown control fuse(if there is one), a fried circuit/logic board, or tstat. It's hard to comprehend that the contacts on a relay would fail and leave the electronic components of the system intact unless there is some type of substantial current limiting function engineered into the electronic components. I doubt it based on the number of circuit boards I've seen fried.
As GlennH suggested, you can always insert a 3amp non-time delay control fuse in the secondary and see what happens.
Also, mrcanby suggested installing a relay to isolate the HVAC control circuit from the FA switch loop, not a bad idea and quite common in many control applications. In fact, large, top of the line equipment has this feature built into the control scheme.
As far as the FA relay is concerned, what is the resistance across the closed contacts, what is the voltage drop across the contacts under full load(FOP), what is the current draw on the line side vs the load side of the contacts?
Good luck and be sure to let us know how this turns out...I'm currious now.