Can I put three sets of single phase 120/208 in a race way for three separate RTUs without creating heat if voltage drop is not an issue and pipe is sized probably? Iam trouble shooting a heat problem in an Hvac panel ! Breaker opens and all four Breaks are hot!?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Sure you can as long as the conductors are sized properly but with heavy loads you will always have heat. That means you have 6 current carrying conductor's so you would have to de-rate 80% of the ampacity of the conductor.

You said 3 RTU's but then said 4 breakers???? How many are tripping, what size wire, and what is the mca of the units.
 

Tom G

Member
Location
Hartand Wisconsin
Occupation
Electrical worker
Yes three sets in one pipe and a 4th in another! One breaker trips often and panel is really warm. Could be length or run. Possibly voltage drop problem.? 350 feet thank you for your reply!,
 
Last edited:

Tom G

Member
Location
Hartand Wisconsin
Occupation
Electrical worker
Depends.

Were the wires sized correctly to begin with?

Temperature is subjective.
Could be improperly torque connections at the breaker.
Breaker stabs not making good contact.
Overload due to equipment malfunction.
Depends.

Were the wires sized correctly to begin with?

Temperature is subjective.
Could be improperly torque connections at the breaker.
Breaker stabs not making good contact.
Overload due to equipment malfunction.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Are the conductors heavy enough to be conducting heat from within the conduit to the breakers?

You never answered any of our questions about the units' numbers and the wire sizes.
 