air conditioning sizing conductors

Status
Not open for further replies.
i havent done much sizing of conductors for AC/heating units, but reading 440.2 definitions of 'branch circuit selection current' I thought there was another chart like they had for motors in sizing conductors, but apparently not. You just follow the nameplate rating and mulitply 125%. Correct me if im wrong please. and if this is the case why couldnt they just worded it 'simplier' in the NEC. Basically you can have a #12 awg on a 40 amp breaker if the numbers are right!!

I had to correct a guy when he was getting upset about an AC unit that had #12 awg on a 30 amp.

Thanks.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If I understand Art 440 correctly, 440.6 advises to select a conductor by its ampacity from 310.16-19 with that ampacity requirement designated by 440.4 and displayed by the manufacturer.
I do not see any requirement for a 125% multiplier.
Likewise 440.21(C) limits the maximum breach circuit protective device based on manufacturers data.
 
If I understand Art 440 correctly, 440.6 advises to select a conductor by its ampacity from 310.16-19 with that ampacity requirement designated by 440.4 and displayed by the manufacturer.
I do not see any requirement for a 125% multiplier.
Likewise 440.21(C) limits the maximum breach circuit protective device based on manufacturers data.


The 125% comes from 440.32
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
440.32 doesn?t apply to typical A/C equipment. 440.32 is for a single motor compressor not multi motor equipment. The manufacture has already the 125% to the MCA marked on the unit.
 

iMuse97

Senior Member
Location
Chicagoland
this unit is a single motor compressor, other than the fan motor, its a condensor.

I think what C. Swartz is saying: a typical A/C compressor/condenser unit has two motors, and has a minimum circuit ampacity listed on the nameplate which is used to size the wire to the unit. You do not multiply this number by 1.25; you just use wire that will carry that ampacity, with any derating or correction factors figured in.

In addition, I would add that on any newer equipment the nameplate will also list maximum breaker size.
 
Last edited:

billsnuff

Senior Member
In addition, I would add that on any newer equipment the nameplate will also list maximum breaker size.

I seem to recall breaker or fuse, depending what is spec'd on the unit tag, or am I all wet. ( i.e. if it says fuse you can't use breaker?)
 

dcspector

Senior Member
Location
Burke, Virginia
I seem to recall breaker or fuse, depending what is spec'd on the unit tag, or am I all wet. ( i.e. if it says fuse you can't use breaker?)

Most list either or however some Mitsubishi units show fuse only and or different fuse size versus breaker size.? I am guessing here must be due to differing AIC ratings between the two (fuse vs. breaker)
 
Location
New jersey
The name plate gives you 125% of largest motor and 100% of all others. The min circuit ampacity is your wire size (you can use #14 for 20amps #12 for 25 amps) Then the max fuse or circuit breaker is marked on the name plate. I have seen some units that you could wire with a #14 and protect with a 30 amp breaker.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Things are changing fast. I have noticed that the higher seers rated a/c seem to have a small difference bewteen MCA and MOCP. My last unit called for a MCA of 12 amps with a max OCP of 15 amps.

Those older units would allow a MOCP of 20 or 25 amps.
 