tacomafc
Senior Member
- Location
- Long Island New York
Could you please let me know if i'm reading the exception correctly in the code book. I have to feed a air condensor unit. The name plate on the unit says
min. cir ampacity (28 amps) and the max. over current protection is (50 amps).
Sounds CRAZY but I think I could use a 10 awg wire and a 50 amp circuit breaker.
min. cir ampacity (28 amps) and the max. over current protection is (50 amps).
Sounds CRAZY but I think I could use a 10 awg wire and a 50 amp circuit breaker.