Does this look correct for the branch circuit wiring and OCPD for an air curtain with (1) 20 kW heater @ three phase, 208V + (2) motors @ single phase, 208V, FLA 3.6 amps each.
Branch circuit conductors:
20 kW / 360 = 55.6 A
3.6 x 1.25 = 4.5 A
3.6 x 1.00 = 3.6 A
Conductors = 63.7 = MCA
OCPD (circuit breaker):
55.6 + 3.6 x 2.5 + 3.6 = 68.2 = 70 A C.B.??
Branch circuit conductors:
20 kW / 360 = 55.6 A
3.6 x 1.25 = 4.5 A
3.6 x 1.00 = 3.6 A
Conductors = 63.7 = MCA
OCPD (circuit breaker):
55.6 + 3.6 x 2.5 + 3.6 = 68.2 = 70 A C.B.??