Air curtain sizing branch circuit & OCPD

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
Does this look correct for the branch circuit wiring and OCPD for an air curtain with (1) 20 kW heater @ three phase, 208V + (2) motors @ single phase, 208V, FLA 3.6 amps each.

Branch circuit conductors:

20 kW / 360 = 55.6 A
3.6 x 1.25 = 4.5 A
3.6 x 1.00 = 3.6 A

Conductors = 63.7 = MCA

OCPD (circuit breaker):

55.6 + 3.6 x 2.5 + 3.6 = 68.2 = 70 A C.B.??
 
Do you mean the 3.6?

The datasheet says 208/230V and lists 3.6 A, even though it should be 3.2 according to the NEC table.

Just reread it. The 360 came from 208 * 1.732
 
Does this look correct for the branch circuit wiring and OCPD for an air curtain with (1) 20 kW heater @ three phase, 208V + (2) motors @ single phase, 208V, FLA 3.6 amps each.

Branch circuit conductors:

20 kW / 360 = 55.6 A
3.6 x 1.25 = 4.5 A
3.6 x 1.00 = 3.6 A

Conductors = 63.7 = MCA

OCPD (circuit breaker):

55.6 + 3.6 x 2.5 + 3.6 = 68.2 = 70 A C.B.??

I don't think a 70A branch circuit breaker will provide proper for a 1/4HP 208V single phase motor.

If the calculation was for a motor feeder, (or a branch circuit in accordance with 430.52(C)) the calculation would actually be 55.6 + 3.6 + 15 =74.2 => which is an allowable 70A c/b. (sized down, not next size up.) The 15 is the allowable ocpd size for one of the motors.
 