Air handler 240v 2.5 ton

Status
Not open for further replies.

rydan

Member
Location
RPB, Fl.
A/C guy just installed a new air handler and is needing a 220 line run to it .. He said the unit is 2.5 tons but the handler needs a #6 wire run to the unit ????? Its about 18ft from the panel in the attic... I was told to just run a #10 wire and a 2 pole 30 for it ... Who is right ????
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The air handler with NO heat would likely be less than a 10 amp load.
The answer to your question relies on the size of the heat strips installed.
A air handler with a 10kw heat strip can often be fed by a #6 but depending on the exact numbers may require a #4 in NM cable.
You need more input. The air handler should have a nameplate giving the minimum circuit amps.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Likely somewhere in the neighborhood of a 45 amp circuit requirement so your #6 NM should be fine.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
8kw @ 240 volts is 33 amps. What does the nameplate of the unit say?

( Explaination to OP, I used the 33 amps adjusted by 1.25 per 424.3(B) + a guessimated motor load as infinity notes, go by your nameplate numbers))
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
( Explaination to OP, I used the 33 amps adjusted by 1.25 per 424.3(B) + a guesstimated motor load as infinity notes, go by your nameplate numbers))

I figured that was how you got the 45 amps. Sounds like a good guesstimate. :)
 