Residential HVAC system. Air handler in attic of a ranch home. Heat pump. Outdoor unit.
Having a problem with the air handler circuit.
There is one feed to the air handler - a #6 AWG 2-wire copper feed with ground. 60 ampere square D breaker in distribution panel in garage. Another 60 ampere square D breaker at the air handler in the attic. It's a Carrier system.
The circuit goes to a small transformer in the air handler and runs a blower motor. I have tested the current on both conductors while the blower motor is running. The current is about 5 amperes on each leg which seems about right for this little motor.
In the winter, if the heat pump can't do the job (Pennsylvania) there is a 10 kW 2-stage resistance-heat element that kicks in.
I have never had any problems with the resistance heat running in the winter with a current of a little over 40 amperes on the circuit.
The mystery is that in the summer, with only the fan running, I have had a few occasions where the 60 ampere breaker in the attic is tripping. The out-door unit is a separate 30 ampere 240V circuit so it is not involved.
Any thoughts on why this breaker is tripping under a 5-ampere load? I checked connections, no loose connections, no evidence of shorts, the motor turns freely and no smell of burned varnish or anything else. The only factor I can think of is that it happens when it is about 100+ degrees F in the attic.
Everything looks clean around the motor and fan. Replace filters often.
Could the high temperature cause the breaker to trip at such a low current? I believe the system was installed about 20 years ago.
Any help is appreciated. I am considering a new breaker for the attic unit but didn't want to spend 100 dollars unless I have to.
Having a problem with the air handler circuit.
There is one feed to the air handler - a #6 AWG 2-wire copper feed with ground. 60 ampere square D breaker in distribution panel in garage. Another 60 ampere square D breaker at the air handler in the attic. It's a Carrier system.
The circuit goes to a small transformer in the air handler and runs a blower motor. I have tested the current on both conductors while the blower motor is running. The current is about 5 amperes on each leg which seems about right for this little motor.
In the winter, if the heat pump can't do the job (Pennsylvania) there is a 10 kW 2-stage resistance-heat element that kicks in.
I have never had any problems with the resistance heat running in the winter with a current of a little over 40 amperes on the circuit.
The mystery is that in the summer, with only the fan running, I have had a few occasions where the 60 ampere breaker in the attic is tripping. The out-door unit is a separate 30 ampere 240V circuit so it is not involved.
Any thoughts on why this breaker is tripping under a 5-ampere load? I checked connections, no loose connections, no evidence of shorts, the motor turns freely and no smell of burned varnish or anything else. The only factor I can think of is that it happens when it is about 100+ degrees F in the attic.
Everything looks clean around the motor and fan. Replace filters often.
Could the high temperature cause the breaker to trip at such a low current? I believe the system was installed about 20 years ago.
Any help is appreciated. I am considering a new breaker for the attic unit but didn't want to spend 100 dollars unless I have to.