bphgravity
Senior Member
- Location
- Florida
Consider a typical residential air handling unit used in a single family home. (The unit employs supplementary overcurrent devices, a blower motor and heating elements.)
The NEC requires a disconnecting means for the unit. Which section is applicable for determining the location of the disconnecting means?
1. Section 422.30
2. Section 424.19
3. Section 430.101
The specific issue deals with a particular builder that installs the air handler in a closet inside the home. There is no adequate space for a disconnecting means inside the closet. The builder does not want the disconnecting means on the outside of the closet.
I feel the only option to provide a "unit switch", which the particular air handler is designed for this application or a locking device could be provided at the branch circuit panelboard in the garage. I feel this is permitted by Section 424.19(A)(2)(2).
The NEC requires a disconnecting means for the unit. Which section is applicable for determining the location of the disconnecting means?
1. Section 422.30
2. Section 424.19
3. Section 430.101
The specific issue deals with a particular builder that installs the air handler in a closet inside the home. There is no adequate space for a disconnecting means inside the closet. The builder does not want the disconnecting means on the outside of the closet.
I feel the only option to provide a "unit switch", which the particular air handler is designed for this application or a locking device could be provided at the branch circuit panelboard in the garage. I feel this is permitted by Section 424.19(A)(2)(2).