DM2-Inc
Senior Member
- Location
- Houston, Texas
With respect to buildings located in Class I, Division 2 locations that use I'm trying to find out where, or if, there is a required height above grade that air used to pressurize a building must come from. Most of the buildings we see have a stack that take are into the pressurization system from about 25 feet above grade (or there about). I thought I'd see this in Chapter 7 or 8 of NFPA 496 but I don't see it there or in the Annex material.
If it's not specifically called out, how does one go about determining where to take the air from?
If it's not specifically called out, how does one go about determining where to take the air from?