aircraft fuel farm NEC

Status
Not open for further replies.

mjmike

Senior Member
Was reviewing NFPA 407 for aircraft fuel farms (2017 edition). Smaller skid mounted units. NFPA 407 5.1.6.1 indicates NEC 515 must be follows and considered class 1 liquids. Looking at 515 (2011 edition), it appears it is more intended for a facility that processes or stores bulk fuel; like a refinery. It does not appear to be related to a fuel farm at an airport. However, it does not appear you can be in compliance with the NFPA if you don't follow NEC 515. Is this being read correctly, what would the fuel farm fall under?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
The distinction is not so much the volume of the tanks, but the means of delivery and distribution. Basically a tank farm is a tank farm and, unless you can show the fuel is not a Class I flammable liquid, Article 515 applies.
 