Appreciate your replies, always amazing how it helps to have someone else reading to direct one to the right conclusion when dealing with the NEC.
RB1 said:The entire area of the hangar is required to classified. The classification does not extend into areas that are suitably cut off (513.3(B)). Areas that have communicating openings into the hangar space are required to be classified unless ventilated (513.3(D)).
It is interesting that the title of 513.3(D) reads "Suitably Cut Off and Ventilated" but if the area is cut off, and is not required to be classified in the first place, why would you need ventilation?
RB1 said:Therefore areas that are suitably cut off are not classified.
RB1 said:Steve how did the vapors build up through an unpierced partition?