Aircraft Hanger

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is there any requirement in any Code requiring a ground ring at an aircraft hanger. There are plans showing a 4/0 ground ring with 2/0 tails to structural steel. AFIK it's an engineering requirement but Ive been asked if it's in any Code.
T
 
Is there any requirement in any Code requiring a ground ring at an aircraft hanger. There are plans showing a 4/0 ground ring with 2/0 tails to structural steel. AFIK it's an engineering requirement but Ive been asked if it's in any Code.
T
That was a common industrial spec, but not in the NEC.
 
Is there any requirement in any Code requiring a ground ring at an aircraft hanger. There are plans showing a 4/0 ground ring with 2/0 tails to structural steel. AFIK it's an engineering requirement but Ive been asked if it's in any Code.
T
That’s a customer specification. I have never done an aircraft hanger but I have read about that. Also a standard in carrier CO and cellular. Typically connection means is exothermic (Caldweld) I would not deviate from the drawings without getting it in writing from the customer. Are the drawings stamped?

Charge for the work and make money on it!
 