Is there any code articles that govern airport ltg. and safety issues re:constant current regulators 5KW-30KW establishing approx. voltage of 1000-5000/w a current output of 6.6 amps , approx. 100 runway or taxiway lights?
Is there any code articles that govern airport ltg. and safety issues re:constant current regulators 5KW-30KW establishing approx. voltage of 1000-5000/w a current output of 6.6 amps , approx. 100 runway or taxiway lights?
I never realized code articles covered airfield ltg. Thanks. Also manholes w/ duct banks entering and leaving, when entering this manhole do need to lock all live crkts.?this is the only i know off hand
310.7 Direct-Burial Conductors.
Conductors used for direct-burial applications shall be of a type identified for such use.
Cables rated above 2000 volts shall be shielded.
Exception No. 1: Nonshielded multiconductor cables rated 2001?2400 volts shall be permitted if the cable has an overall metallic sheath or armor.
The metallic shield, sheath, or armor shall be connected to a grounding electrode conductor, grounding busbar, or a grounding electrode.
Exception No. 2: Airfield lighting cable used in series circuits that are rated up to 5000 volts and are powered by regulators shall be permitted to be nonshielded.
FPN to Exception No. 2: Federal Aviation Administration (FAA) Advisory Circulars (ACs) provide additional practices and methods for airport lighting.
FPN No. 1: See 300.5 for installation requirements for conductors rated 600 volts or less.
FPN No. 2: See 300.50 for installation requirements for conductors rated over 600 volts.
For the 2008 Code, the requirements for grounding the metallic shield have been clarified and more specifically stated. In addition, the revised Exception No. 1 limits the omission of shielding up to the 2.4-kV level only for direct burial conductors. In coordination with present Federal Aviation Administration provisions for airfield lighting cable, Exception No. 2 is new, permitting certain circuits up to 5 kV to be unshielded as well. See 310.7, Exception No. 2 and the associated fine print note for specific provisions and original source material.
I would bet the FAA has something to say.
I think the FAA has the only say. They have their own inspectors.
Also manholes w/ duct banks entering and leaving, when entering this manhole do need to lock all live crkts.?