Al/Cu splice repair for air conditioner power

Status
Not open for further replies.
There is an open circuit in a junction box where the copper wire from our panel connects to the aluminum wire to our air conditioner.

The power for our air conditioner leaves our circuit breaker panel through a dual 50 Amp breaker. I believe the wire is stranded #6 AWG copper. It is connected in a junction box to what I believe is #4 AWG stranded aluminum wire. (I am going to measure the wire diameters tomorrow to verify the gauges). The house was built in 1976 and I believe the wiring dates from then. I will post a picture of the box and the wires tomorrow

One of the wire nuts disintegrated to the point that I couldn't find any remnants of it. There was a lot of soot on and around the box which made it look like it was destroyed in a high heat event. The wire nut that is still in place on the other hot supply wire looks like it was some kind of specialized connection device (it looks sort of like a wire nut but it appears to have been crimped) that was used because of the connection was an aluminum to copper connection. I think there was a wire nut on the ground wire but I don't remember the details of it right now.

Assuming my estimate of the wire gauges is correct I plan to use three Polaris 4-14 gauge tap connectors (IT4) (https://images.homedepot-static.com/catalog/pdfImages/ff/ff091f1c-8580-4bcd-a922-6374ecac582e.pdf) to make the connections. I saw a thread on a similar issue and split bolts were suggested. The Polaris looks to be much simpler to me and I don't mind the extra cost. How important is a torque wrench to get the screw torque correct?

If there is not room in the 4 inch junction box I plan to use a junction box extender.

The original installer stripped the wires back too far and there was about 1.5 inches of exposed copper wire on each wire in the box. He seems to have carefully assembled the wire in the box so that they didn't short (perhaps there was enough heat in the box that the insulation shrank back from the connection?). I plan to fix this by covering the exposed wire with heat shrink tubing. I plan to use the grey goop on the aluminum wires recommended for aluminum connections.

As an aside, the junction box seems to have done its job. It looks like the event that destroyed the connector might have produced enough heat to have started a fire if the connection had not been contained within a junction box.

Thank you for any comments and help. It will be greatly appreciated.

-Dave
 
Thanks for the response. FWIW, I've installed quite a bit of 12 and 14 gauge wire over the years. I have never dealt with wires with this heavy a gauge before and this is only the second time I've dealt with aluminum wire.

This is an image of the junction box:
IMG_2625.jpg

The diameter of the aluminum and copper wires was about 5mm. They were stranded. I assume they were #4 AWG.

The run of copper wire from the panel is about 20 feet. The run to the air conditioner is about 20 feet.

I was wrong that some kind of specialized wire nut type connectors had been used. Regular wire nuts for the connections seem to have been used. The one that I thought wasn't a wire nut had just been badly damaged so I didn't recognize it right away as a wire nut. The missing one seems to have been vaporized.
 
Are you certain you have aluminum conductor? As hot as that appears to have been I don't think the intact conductor would be in as good of shape as it is in if it were aluminum? If it is silver colored might be tin plated copper.

Also doesn't look like anything is 4AWG. That size is nearly impossible to tuck into a 4 inch square box, and I don't know of any "wire nuts" that would accept a 4 and a 6 AWG very well at all. Maybe if the 4 is compact conductor it would.

You are going to want to cut conductors back to a point where they haven't been heat damaged (copper or aluminum doesn't matter) or this problem may come back anyway.
 