AL feeder connect to CU bus bar

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Thought incoming AL wires that feeds an electrical panel won't work well with CU bus bar, the bus bar must be dual rate (AL/CU).
Or bus bar can be CU but wire lugs must be dual rate (AL/CU)?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Thought incoming AL wires that feeds an electrical panel won't work well with CU bus bar, the bus bar must be dual rate (AL/CU).
Or bus bar can be CU but wire lugs must be dual rate (AL/CU)?
The AL wires are connected to the lugs. If the lugs are suitable for AL you are good.
 