AL Feeder Tap Sizes

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
I'm not 100% clear if what they are asking for is correct. Tapping extg. feeder to feed 400A MDP-6. Note #3 is asking for (6) #300 Al & 1 #300N. My questions.

According to ampacity of #300Al it looks like this is (2) sets each containing a 3#300 hots and 1 #300 neutral.
They don't ask for a ground, shouldn't they?

Thanks.
 

Attachments

  • Feeder Tap 1.jpg
    Feeder Tap 1.jpg
    14.8 KB · Views: 0
  • Feeder Tap 2.jpg
    Feeder Tap 2.jpg
    14.7 KB · Views: 0
  • Feeder Tap 3.jpg
    Feeder Tap 3.jpg
    8.6 KB · Views: 0

mstrlucky74

Senior Member
Location
NJ
Guess it is just one 4". Never seen this configuration but the 6 conductors can fit. Why no ground?
 

Attachments

  • Capture.jpg
    Capture.jpg
    10.3 KB · Views: 0

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Each Ø is comprised of 2-300 kcmil conductors, the neutral load is small so there is only 1-300kcmil neutral. With the 80% derating adjustment your adjusted ampacity is 2 * 260 amps * 80% = 416 amps.
 

iwire

Moderator
Staff member
Location
Massachusetts
Yes i know but hey then do so many feeders have a ground with them? Thanks

Why are some cars blue and some white?

Personal choice, perhaps an issue with fill?

I have chosen to use the conduit as the EGC to reduce the pipe size needed.

It used to be common to do so, now people get all freaked out when you do it. :D
 