HYPOTHETICAL QUESTON . can you splice al to cu in a listed junction box with WAGOS to make service conductors longer ????????????????????????????????????????????????????????????????
But you know the answer to this already like most of us do.1. Are Wagos rated for aluminum? If yes, then yes.
2. Are Wagos suitable for services? If yes, then yes.
3. Do they make Wagos that big? If yes, then yes.
If the answer to all three is yes, then yes.
Yes indeed. To the OP - you mention Service Conductors in the original post. Are you, perhaps, trying to extend branch circuit wiring?Keep in mind everyone's favorite 230.46 (if these are indeed service conductors he's talking about).
SORIY I MEANT TO SAY POLARIS!!!!HYPOTHETICAL QUESTON . can you splice al to cu in a listed junction box with WAGOS to make service conductors longer ????????????????????????????????????????????????????????????????

Since my company closed up, and I don't have an account any more at most supply houses - I can see they don't give me the best prices anymoreMy cost for the NSI-Polaris IT-250C is $17
I'm thinking all the connector manufacturers seen what the AFCI/GFCI manufacturers have done and wanted to get in on some of the action as well, though this is kind of minor in comparison to the AFCI/GFCI thing.Back to the OP, now that we clarified these are indeed service conductors: Sure no problem, but keep in mind that depending on what code cycle you are on, connectors on the line side of the service disconnect may need to be listed for that use. What happened was, the CMP's needed to come up with some other stupid new codes after the AFCI's and SPD's. Not wanting to make some much needed real changes like getting rid of some of the grounding and bonding BS in 250, they continued with the stupid stuff and picked something that had no history of problems or issues and is completely arbitrary. There wasnt even a standard to list them too for a long time. Some products are trickling onto the market, but there still are not that many.
WE do it , nothing wrong with it . it is code compliant ! what do you not like about it .whatever you do don't splice service wires if you can avoid it.
Not cost effective usually with small residential services.WE do it , nothing wrong with it . it is code compliant ! what do you not like about it .
Also depends on the amount of labor needed to replace an entire run.Not cost effective usually with small residential services.
120 bucks in splices buys like 35 ft of 4/0 4/0 2/0
True but what are we looking at in a de-energized service in pipe so 1 hour labor or so i think 3 polaris will take almost as long if using a tourqe wrench and making it up nice and clean. Maybe if a cable service entrance it could be worth it but I hate using those and prefer something in some sort of raceway for this peticular part of the electrical system.Also depends on the amount of labor needed to replace an entire run.