Al

Status
Not open for further replies.

dlhoule

Senior Member
Location
Michigan
Yes, there is. Old abandoned cables are supposed to be removed unless labeled for future use.

This is something that is very rarely enforced.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Okay Barbeer-- spill the beer, I mean beans

spilled_beans_off_white.gif
 
Last edited:

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Alberto Galvan said:
Is there anything in the code book on abandonement of old cables.
Low voltage cables, as is security, cable TV, perhaps even telephone, yes. Power cables, as in power to 120 volt general purpose receptacles, no.
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Checked the time...800.2, 640.2, 725.2, 760.2,820.2, and 830.2 all talk about abandoned cable.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You see--- I was thinking about mc cable ,nm cable etc. I always thought they just needed to be terminated in a jb and covered but not removed. Is that correct? and where is that reference, if you know?
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Stands up...shakes self off from avalange of replys per threat of thunder theft and heading out for lunch!
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Dennis,

I've always just capped them off because the removal of systems still standing, normally meet the fire withstand rating of fifteen minutes, I believe, is part of the logic. Communcation cables are "open" to exposure in the their nature in a building.
 

barbeer

Senior Member
Dennis - I agree with you, however, 760.3(A) references 300.21 and depending on how much "grey" matter you posess you could correlate that article to mean the same as the previously posted.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Don't miss the point that Charlie brought up. That spaghetti bowl of MC or AC cable above a hung ceiling is permitted to remain even if it's unused and untagged.
 
Status
Not open for further replies.
Top