I found a 100amp electric service today with a meter and panel all in one with a removable bond jumper.
I thought all in ones were all suitable only for use as service equipment and had bonded neutrals.
Also the jumper is a #12 conductor.
The supplier tells me it is all factory installed and according to the UL listing.
Does this sound right to any one?
I thought all in ones were all suitable only for use as service equipment and had bonded neutrals.
Also the jumper is a #12 conductor.
The supplier tells me it is all factory installed and according to the UL listing.
Does this sound right to any one?