210811-1326 EDT
sparky1118:
Your posts are not an adequately clear description of your problem.
All I can determine from your posts is that ---
1, You have at least one light that flickers.
2. You have at least one dimmer somewhere, probably a phase shift dimmer.
For testing purposes I would like you to have ---
1. A good digital meter like a Fluke 27.
2. A good analog meter like a Simpson 260 or 270.
3. A 1500 W space heater.
4, A non dimmable CREE 9 W LED.
5. A 15 W tungsten incandescent bulb,
6. A good digital oscilloscope, and probes.
7. Suitable sockets and test leads.
Which of these you use and need will depend upon how the tests progress.
The CREE bulb will show very little flicker until large voltage changes occur.
The incandescent takes about a 2 V change to be noticeable.
The 1500 W 120 V heater produces about a 12 A load when warmed up.
With the digital meter ( I suggest the Fluke 27 instead of the 87 because the 87 resolution makes reading more difficult ) measure at the main panel relative to neutral each phase voltage, and to a screwdriver poked int the earth outdoors. Put the meter test leads directly on the incoming wires, not the terminating lugs. Then also make a hot to hot voltage measurement. You might watch each of these voltages for a short time to see how much typical fluctuation occurs. The changing voltage might be from house loads or power company variations.
Next do the same tests again, but with the 1500 W heater cycled on and off. And I mean with the voltmeter probes looking at the incoming lines. May not matter what circuit the heater is on. At my home the unloaded phase increases by about 0.3 V and the loaded phase drops about 0.7 V. This serves as a base reference.
Assume you have a single dimmer in question and an associated bulb for that dimmer. Set the dimmer at one point such that flicker is observed. At this time we don't not know what causes the flicker.
Cycle the heater on the opposite phase from the phase that the flickering light is on. This time I would suggest that the heater be connected directly at the main panel to eliminate a common neutral from the main panel between the heater and the light circuit. I did not mention above that measurements also be made inside the main panel after fuses and brokers. But, if there is a problem in the main panel you can do these tests later. If any flicker were to occur it should be an increase in light.
Change the heater to be on the same phase as the flickering light, but not is breaker.
At the main panel it would be good to measure the voltage from neutral to the output of the breaker that goes to the flickering light. Does this change enough to cause flickering?
Report back on whether these tests tell us anything.
.