Here is an interesting problem I was called to check a few years ago. Call was outside receptacles not working. I checked all the receptacles that I was shown and all were dead. It was kind of confusing as to where they were fed from. Most of the receptacles were on the side of the house but some were on the side of the garage about 10' from the house. There was a house panel and one in the garage. So I checked both panels and there were no breakers that didn't have power on the load side. So I was pretty sure there was a GFCI tripped somewhere.
I took out one of the receptacles and confirmed my suspicion that they were fed from a GFCI receptacle as there was no continuity between the neutral and EGC. So I started my search by going to all the receptacles that I was shown. Still no GFCI found. So I started looking behind things both in the house and garage. I finally found a GFCI in the garage behind some shelves and it was tripped. Great, I found the problem! I checked all the receptacles inside and outside the garage and they were all now working. Good, job well done!
Not so fast! Job not finished as the receptacles on the house are still not working. Went back and checked the GFCI in the garage and it was still working. So now I've determined that I was dealing with two problems and two circuits. I checked another receptacle and found the same as before, no continuity from neutral to EGC. So I knew there had to be another GFCI. I checked again and still saw no GFCI or one that was tripped anyway. After more searching, I finally found the problem and it was mostly what I thought, a tripped GFCI. But I bet no one can guess what caused it.
I will wait a bit to give the solution to this but I want to see what some of your thoughts are before revealing it.
One clue, it was not a ground fault causing the trip, nor a faulty piece of equipment.
I took out one of the receptacles and confirmed my suspicion that they were fed from a GFCI receptacle as there was no continuity between the neutral and EGC. So I started my search by going to all the receptacles that I was shown. Still no GFCI found. So I started looking behind things both in the house and garage. I finally found a GFCI in the garage behind some shelves and it was tripped. Great, I found the problem! I checked all the receptacles inside and outside the garage and they were all now working. Good, job well done!
Not so fast! Job not finished as the receptacles on the house are still not working. Went back and checked the GFCI in the garage and it was still working. So now I've determined that I was dealing with two problems and two circuits. I checked another receptacle and found the same as before, no continuity from neutral to EGC. So I knew there had to be another GFCI. I checked again and still saw no GFCI or one that was tripped anyway. After more searching, I finally found the problem and it was mostly what I thought, a tripped GFCI. But I bet no one can guess what caused it.
I will wait a bit to give the solution to this but I want to see what some of your thoughts are before revealing it.
One clue, it was not a ground fault causing the trip, nor a faulty piece of equipment.