Has anyone had an A/B VFD go bad by burning out internal dc bus components? Size of our motor is 50Hp. Application is a large volume pressure washer unit. Our ramp time is 3 seconds and we have NO DC braking resistor. We have lost 3 VFD's. We had a visit from an A/B tech rep and followed his suggestion's. Jumpers were checked for internal configuration on an ungrounded 460 V Delta system.......A line reactor was installed. Power in was monitored for quality. Still we have lost another one.
My question is.....Is it possible to have the ramp up and down so fast that it would cause an excessive DC Buss Voltage big enough to burn out the internals of the VFD. We once again have NO Braking Resistor.
We will be doing one or more of the following:
Slowing the ramp time......Oversizing the VFD.......Installing the Braking Resistor........Isolation Transformer......
But for now frozen in time before we do those things I am wondering if the design guys would have had this happen in the test lab and confirm when a braking resistor would be needed?
We have 2 of the units with the A/B forensics (research) department evaluating them.
Has anyone had an A/B VFD go bad by burning out internal dc bus components? Size of our motor is 50Hp. Application is a large volume pressure washer unit. Our ramp time is 3 seconds and we have NO DC braking resistor. We have lost 3 VFD's. We had a visit from an A/B tech rep and followed his suggestion's. Jumpers were checked for internal configuration on an ungrounded 460 V Delta system.......A line reactor was installed. Power in was monitored for quality. Still we have lost another one.
My question is.....Is it possible to have the ramp up and down so fast that it would cause an excessive DC Buss Voltage big enough to burn out the internals of the VFD. We once again have NO Braking Resistor.
We will be doing one or more of the following:
Slowing the ramp time......Oversizing the VFD.......Installing the Braking Resistor........Isolation Transformer......
But for now frozen in time before we do those things I am wondering if the design guys would have had this happen in the test lab and confirm when a braking resistor would be needed?