I work at a liquid nitrogen plant. When the plant was constructed one of the PLC panels utilized only a single 5A fuse to protect all of the 16 outputs on the relay cards.
The issue we have encountered (3x now) is that some of the pneumatic actuated valves are solenoid controlled, and we have had solenoids short out and wipe out all outputs on that card wreaking havoc to the process / automation. Not sure why the solenoids are failing, it could be partly due to the harsh environment they are installed.
I was just curious if there was a standard for sizing fuses for these outputs? they are all 24VDC @ 10 watts. (417mA)
Thinking of leaving the 5 AMP branch fuse in place and adding 1 amp fuses to each of the 16 outputs to minimize downtime and speed up troubleshooting. Is it worth it using the time delay fuses? My thoughts are that 1 AMP fast acting is more than adequate for each of the individual outputs, as the coil current should in theory never change even if the valve jams.
The issue we have encountered (3x now) is that some of the pneumatic actuated valves are solenoid controlled, and we have had solenoids short out and wipe out all outputs on that card wreaking havoc to the process / automation. Not sure why the solenoids are failing, it could be partly due to the harsh environment they are installed.
I was just curious if there was a standard for sizing fuses for these outputs? they are all 24VDC @ 10 watts. (417mA)
Thinking of leaving the 5 AMP branch fuse in place and adding 1 amp fuses to each of the 16 outputs to minimize downtime and speed up troubleshooting. Is it worth it using the time delay fuses? My thoughts are that 1 AMP fast acting is more than adequate for each of the individual outputs, as the coil current should in theory never change even if the valve jams.