liquidtite
Senior Member
- Location
- Ny
is the 90* column for table 310.16 for d- rateing.? and do you use the 60* column for thhn or the 75* chart.or does it matter at what temp you will be apllying the insulation under
is the 90* column for table 310.16 for d- rateing.? and do you use the 60* column for thhn or the 75* chart.or does it matter at what temp you will be apllying the insulation under
so will it tell you on the nameplate rateing what degree it shall be terminated at .allong with ocps
is the 90* column for table 310.16 for d- rateing.? and do you use the 60* column for thhn or the 75* chart.or does it matter at what temp you will be apllying the insulation under
Nothing wrong with yours and others statements, for the most part.The temperature rating is not limited to the conductor insulation, and equipment. It is dependent on all portions of the circuit and components of the circuit.
1. the enclosure rating
2. conductor insulation rating
3. Overcurrent rating
4. equipment rating
5. and any other component in the system
*Take a look at the temperature rating of PVC.
There may be portions of the circuit rated at 90degree C, but the weak link is what the circuit will be rated at. I am positive that all enclosures are rated at 75degree C. Most if not all circuit breakers are rated at 75degree C. And as has been mentioned, the last sentence of 110.14 is where we will find the temperature rating of the conductor insulation for final ampacity application is 75Degree C.
how could their be so many factors involving allowable ampacities of insulated conductors? how do u put all those factors into it and come up with a final ampacity for that insulationThe temperature rating is not limited to the conductor insulation, and equipment. It is dependent on all portions of the circuit and components of the circuit.
1. the enclosure rating
2. conductor insulation rating
3. Overcurrent rating
4. equipment rating
5. and any other component in the system
*Take a look at the temperature rating of PVC.
There may be portions of the circuit rated at 90degree C, but the weak link is what the circuit will be rated at. I am positive that all enclosures are rated at 75degree C. Most if not all circuit breakers are rated at 75degree C. And as has been mentioned, the last sentence of 110.14 is where we will find the temperature rating of the conductor insulation for final ampacity application is 75Degree C.
how could their be so many factors involving allowable ampacities of insulated conductors? how do u put all those factors into it and come up with a final ampacity for that insulation
r u saying im a hobbyist
so how do you come up with a final degree to take the insulation at the termination degree is in the 75coloum but the type of insulation si in the 60*
What 110.14(C) does is establish the minimum size conductor that can be used to make the termination, regardless of the conductor's [insulation] temperature rating. It even applies to bare conductors that have no insulation temperature rating. Other sizing (ampacity) requirements can increase the minimum size conductor, but they cannot decrease the minimum size as determined under 110.14(C).so how do you come up with a final degree to take the insulation at the termination degree is in the 75coloum but the type of insulation si in the 60*