E EVPhil New User Location Massachusetts Occupation Electrical Contractor Jan 19, 2020 #1 What is the minimum distance between a 500 gal propane dispensing tank and a NEMA 3R Switchboard 480 volt
What is the minimum distance between a 500 gal propane dispensing tank and a NEMA 3R Switchboard 480 volt
kwired Electron manager Location NE Nebraska Occupation EC Jan 19, 2020 #2 No distance at top of my mind but pretty certain any classified location will be based off of the "dispensing area" and not the tank itself. Any automatic relief valves are also likely to have a classified location around them.
No distance at top of my mind but pretty certain any classified location will be based off of the "dispensing area" and not the tank itself. Any automatic relief valves are also likely to have a classified location around them.
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Jan 21, 2020 #3 The tank is covered in Section/Table 514.3 and possibly Section/Table 515.3 depending on the application. BTW the panel voltage is irrelevant for a power application. The enclosure Type may be, depending on its location. Last edited: Jan 21, 2020
The tank is covered in Section/Table 514.3 and possibly Section/Table 515.3 depending on the application. BTW the panel voltage is irrelevant for a power application. The enclosure Type may be, depending on its location.