Here is the set-up....
A mechanic responded to a lighting circuit that had blown a fuse. In the control cabinet, (6) 2-pole 30A lighting contactors feed (12) fused lighting circuits - 277v, single phase. Blown fuse was a 15A time delay. All other fuses were 20A or 30A time delay. Thinking the 15A fuse was installed incorrectly, mechanic installed 30A time delay fuse to restore circuit. No special labeling indicating any fuse size withing the cabinet. Mechanic was cited for negligent "unsafe work practices" for installing the 30A fuse.
Knowns:
Circuit draw is - less than 9 A
Each light pole protected with 2 Amp fuses at base of pole
All contactors protected with up-stream 30A double pole circuit breakers
#10 solid THHW wiring throughout cabinet and branch circuits to poles
Aside from voltage drop calculations (which should have been considered at install), no special labeling for required fuse size, or conduit fill de-rating (again, install calculations)... all of which are unknown to a maintenance mechanic.... I ask the following:
With 30A breakers protecting #10 wiring, and 30A contactors...
Did mechanic violate NEC sectors 240 or 310?
Without specific labeling, was a 30A fuse allowed within the scope of NEC?
With fusing at fixtures, was the circuit under-protected by his actions?
My opinion was no, he did not. From a "users point of view", he based his decision on observable variables, ie. wire size, contactor rating, breaker sixe. Given the circumstances of breaker size, wiring size, no special labeling, and measured load, a 30A fuse was the MAXIMUM he could have gone to.
Was the mechanic negligent? Your thoughts?
A mechanic responded to a lighting circuit that had blown a fuse. In the control cabinet, (6) 2-pole 30A lighting contactors feed (12) fused lighting circuits - 277v, single phase. Blown fuse was a 15A time delay. All other fuses were 20A or 30A time delay. Thinking the 15A fuse was installed incorrectly, mechanic installed 30A time delay fuse to restore circuit. No special labeling indicating any fuse size withing the cabinet. Mechanic was cited for negligent "unsafe work practices" for installing the 30A fuse.
Knowns:
Circuit draw is - less than 9 A
Each light pole protected with 2 Amp fuses at base of pole
All contactors protected with up-stream 30A double pole circuit breakers
#10 solid THHW wiring throughout cabinet and branch circuits to poles
Aside from voltage drop calculations (which should have been considered at install), no special labeling for required fuse size, or conduit fill de-rating (again, install calculations)... all of which are unknown to a maintenance mechanic.... I ask the following:
With 30A breakers protecting #10 wiring, and 30A contactors...
Did mechanic violate NEC sectors 240 or 310?
Without specific labeling, was a 30A fuse allowed within the scope of NEC?
With fusing at fixtures, was the circuit under-protected by his actions?
My opinion was no, he did not. From a "users point of view", he based his decision on observable variables, ie. wire size, contactor rating, breaker sixe. Given the circumstances of breaker size, wiring size, no special labeling, and measured load, a 30A fuse was the MAXIMUM he could have gone to.
Was the mechanic negligent? Your thoughts?