Senior Member
- Location
- Kaukauna, Wisconsin
A few weeks ago we lost power at one of our plants because of a seemingly loose connection between a buss bar and a breaker. 200 Amp 240 Volt single phase breaker. Because the switch gear is quite old, we had an electrical contractor find something that will get us through temporarily, they found a breaker that doesn't match or fit properly but got the lights on so we could run production.
We have been also been tinkering with an Infrared Thermography camera lately. So I curiously looked at the breaker and wires with the camera. Both had elevated temperatures above ambient. Lets say ambient was probably 80?F and the hottest spot was 117?F. An amp clamp showed the breaker was running 137 amps on one phase and 129 amps on the other phase. All of the other 5 breakers and connecting feeders were basically ambient temperature. I am thinking that any temperature rise above ambient should be seen as a problem.
Also these same feeders that were terminated in a panel say 100 feet away also head these elevated temperatures, i.e. the temperature is constant along the length of the conductors as opposed to one hot spot with the heat lessening as it gets further away.
I know that as current runs through a conductor it heats up, but these feeders off the load side of the breaker are 3/0 THHN. In my mind there shouldn't be that much increased heating on these wires or the breaker.
Can anyone shed some light on this issue?
Recently we changed a lot of the lighting in this area of the plant from T12 8' HO fixtures to a T8 4' fixture, utilizing electronic ballasts. I know that these new ballasts can add some heating to the system because of Harmonics.
Other questions rolling around in my head:
We have been also been tinkering with an Infrared Thermography camera lately. So I curiously looked at the breaker and wires with the camera. Both had elevated temperatures above ambient. Lets say ambient was probably 80?F and the hottest spot was 117?F. An amp clamp showed the breaker was running 137 amps on one phase and 129 amps on the other phase. All of the other 5 breakers and connecting feeders were basically ambient temperature. I am thinking that any temperature rise above ambient should be seen as a problem.
Also these same feeders that were terminated in a panel say 100 feet away also head these elevated temperatures, i.e. the temperature is constant along the length of the conductors as opposed to one hot spot with the heat lessening as it gets further away.
I know that as current runs through a conductor it heats up, but these feeders off the load side of the breaker are 3/0 THHN. In my mind there shouldn't be that much increased heating on these wires or the breaker.
Can anyone shed some light on this issue?
Recently we changed a lot of the lighting in this area of the plant from T12 8' HO fixtures to a T8 4' fixture, utilizing electronic ballasts. I know that these new ballasts can add some heating to the system because of Harmonics.
Other questions rolling around in my head:
- Knowing that breakers and fuses operate on basically heat generated by current, how hot should a conductor get say at 50%, 75%, 90%, 100% ampacity? I know there are a lot of variables included in answering this question properly, but generally speaking, what could one expect. I guess in my mind the temperature of a conductor at 99% ampacity would be pretty close to ambient temperature.
- I know that some manufacturers have allowable temperature rises in the 50?C range and above, but the conductor should be able to safely handle this current for a very long time.
- I have read a little about Harmonics online and it seems to really affect the neutral wire, the lighting in this area is feed 240 volts 1 phase. I don't know if that means Harmonics won't affect it as much.