Ken 6789 said:What is the allowable voltage drop? I've always thought it was 10% max. from trans. to last device on a circuit and 5% max. on motors. Is this correct?
bphgravity said:Check your local building code.
Here in Florida, the Energy Efficiency Code requires a maximum of 2% on feeders and 3% on branch circuits for all non-dwelling occupancies.
hdpeng said:NEC allows up to 3% on feeders, and up to 3% on branch ckts., but not more than 5% total. It's most practical to keep the feeder VD down to 2% (larger conductor/less impedance), and 3% on branch ckts. (smaller conductor/higher impedance).
Good comment about the electric utility side Bob. Most of the public service commissions permit 5% voltage drop in urban areas and 6% in rural areas.iwire said:Which lines right up with the ANSI standard of 5% in the premise wiring system along with 5% on the utility side.![]()
Section 410.300 Voltage Regulation
a) Standard voltage. Each entity supplying electrical energy for general use shall adopt a standard service voltage of 120 volts (when measured phase to neutral) and shall maintain the service voltage within the allowable variations from that value at all times.
b) Allowable voltage variations. For service rendered at the standard service voltage, voltage variations as measured at any customer's point of delivery shall not exceed a maximum of 127 volts nor fall below a minimum of 113 volts for periods longer than two minutes in each instance. For service rendered at voltages other than the standard voltage value, voltage variations as measured at any customer's point of delivery shall not exceed 10% above or below the service voltage for a longer period than two minutes in each instance.
don_resqcapt19 said:While it is nice to say that the utility should stay within 5% . . .