Allowed wires pe box

Status
Not open for further replies.
It's not as simple as that. The answer depends on the presence, or absence, of several things other than wires. It is addressed in NEC 314.16.
 
Take the size of the box and divide by 2.00 cu in/conductor for #14 AWG.

i.e.-32 cu in/2.00 = (16) #14 AWG conductors

This tells you the number of conductors permitted. As Charlie said look at 314.16(B)1-5 for what is counted as a conductor.
 