Alternative bonding

Status
Not open for further replies.

electricalist

Senior Member
Location
dallas tx
Lets say one EC is doing the service , exterior and parking lot and im doing the lease space.
My drawings say the generator is to be bonded to
The CEE ,cold water ,bldg steel and a suplemetal electrode . These being part of the service.
They have 2 ground rods to the service and thats it.
What are my obligations?


Sent from my SM-G360P using Tapatalk
 
Something tells me the EC installing the service is not providing a code compliant GES &/or not following his approved construction documents for the grounding of the building's service. Have you seen the plans for the shell building's service?

If I were you, I would set-up a meeting between you, the service EC, the builder, and the PE's that prepared the two electrical plans to get this all worked out.
 
I was thinking the same.
I asked the other electrician where i could find these service bonds. He replied someone stole them.
Is bldg steel columns ever considered and electrode without knowing if/ proof the J bolts are bonded to rebar?
The slab for the generator has not been poured yet. I was thinking a CEE in the slab that will be connected to the bldg.

Sent from my SM-G360P using Tapatalk
 
I was thinking the same.
I asked the other electrician where i could find these service bonds. He replied someone stole them.
Is bldg steel columns ever considered and electrode without knowing if/ proof the J bolts are bonded to rebar?
The slab for the generator has not been poured yet. I was thinking a CEE in the slab that will be connected to the bldg.

Sent from my SM-G360P using Tapatalk

Just run a #3/0 cu conductor from the steel to the water main. Then you'll know for sure ;)

I use the building steel as a common GEC all the time, but I always bond it to the water main.
 
Lets say one EC is doing the service , exterior and parking lot and im doing the lease space.
My drawings say the generator is to be bonded to
The CEE ,cold water ,bldg steel and a suplemetal electrode . These being part of the service.
They have 2 ground rods to the service and thats it.
What are my obligations?

Your only obligations are what is spelled out in the contract. Anything beyond that is someone else's problem or an extra for you.
 
I asked the electrician doing the services and he said the CEE had been stole then i explained im supposed to bond to it for my generator. I looked friday and it looks like he found a block on the outside with a hole where he could bond to the rebar.
Sometimes it just takes reminding someone.

Sent from my SM-G360P using Tapatalk
 