Alternative to the Myers Hub

Status
Not open for further replies.
Are you terminating conduit to equipment on the inside wall or just passing though wall to equipment further inside? Or stubbing into a transformer room?

Why not just pass though wall and seal with silicone? Silicone is a wonder drug in most cases. Sounds like someone is needlessly overdoing this.
 
Are you terminating conduit to equipment on the inside wall or just passing though wall to equipment further inside? Or stubbing into a transformer room?

Why not just pass though wall and seal with silicone? Silicone is a wonder drug in most cases. Sounds like someone is needlessly overdoing this.
:thumbsup:
 
Is there room to cut squares just big enough for the hubs that can have a thinner chunk of metal bolted to the 1/2" plate and scilicon sealed? Or welded

Getting close!

If fabricating the enclosure - weld a coupling to the enclosure wall. Should be no need for a grounding bushing as the coupling is now effectively a part of the enclosure, can still leave full opening and thread a chase nipple into the interior side if an abrasion bushing is desired.

Winner, winner, chicken dinner! Back in my skid work days in the factory, we welded 3000# couplings to holes in the web of beams to get out of the skid.
 
http://www.cooperindustries.com/con...og-pdfs/conduit-locknuts-sealing-locknuts.pdf

The problem is that these locknuts do not provide a grounding lug.

Several thoughts:
1) Contact Eaton and see if they can supply loose PVC gaskets which could be used with their 'bonding locknuts'.
2) Fabricate a thin sheet metal component with a bonding lug on it, that would fit under the sealing locknut to provide the grounding connection.
3) Simply 'stack' a bonding locknut over a sealing locknut.
On this link I see an option for a four inch bonding locknut, that could replace the locknut for the Myers hub on the inside of the module and use a compression lug on your jumper to go under the screw of the bonding locknut. Looks a lot thinner that a Myers hub locknut giving you some room to play with. A 5" penetration? Makes me wonder if the Myers hub will cover that.
 