Howdy.
I have an Altivar 630 drive running a 300hp motor on a vertical turbine water pump. Drive was a replacement for an Altivar 71 that lost an IGBT and output board before my tenure and the new drive was commissioned by Schneider factory techs last year. We've been having constant problems with the whole setup and it's hard to tell if any of the issues are with the drive or if they're all motor/pump. Drive has input and output reactors. Motor connected by VFD cable which is about 100 feet long. Motor termination is by copper split bolts.
First thing we noticed was that the drive doesn't give the typical VFD whirr noise when running, it just sounds off. This persists even when changing carrier frequency from min to max. Someone decided to leave it at 2kHz. The motor and drive do not get hotter than normal as far as we can tell.
Last year one of the motor-side leads melted inside of the motor junction box. I think it's possible the split bolt terminal was loose, but the motor might have been on its way out considering that a couple months later the motor shorted to ground and we had to get it rebuilt. I don't remember if it was the same phase as the melted wire.
Fast forward 6 months, drive tripped on ground short circuit. I changed carrier frequency to 4kHz according to the manual and double checked all parameters. Then I ran it again and it tripped after 5 minutes. I megged the VFD cable on both sides, megged the motor, and used two different meggers to be sure. I turned the motor shaft by hand and let it spin while I megged the motor. Had the guys who rebuilt our motor send out a tech with a fancy tester to check the windings and insulation. Everything checked out. Re-wrapped the split bolts and put it back in service. Ran for 2 weeks and got another ground short fault. Reset, ran a few days then a motor short fault. Megged everything again, no indication of failure. Put it back in service and it faulted again a few days later.
I've done some searching online for others who have had similar issues. I see people talking about electrical noise, pinholes in wire insulation, heat expansion, and motor vibration. The last one sounds convincing, like the pump is unbalanced or something, considering all the previous issues we've been having and I'd love to know a good (and preferably inexpensive) instrument I can use to log vibration, and if anyone has some pointers on a guide for checking, selecting equipment, peak vs rms etc.
In the meantime we just got a Fluke MDA-550 drive analyzer and once I figure out how to use it, I am going to use it to record the drive. I'm super pressed for time with other projects, so would it be fruitful to check with AND without load on the output and DC bus (4 tests total), or can I save time by checking it just one way or another?
I have an Altivar 630 drive running a 300hp motor on a vertical turbine water pump. Drive was a replacement for an Altivar 71 that lost an IGBT and output board before my tenure and the new drive was commissioned by Schneider factory techs last year. We've been having constant problems with the whole setup and it's hard to tell if any of the issues are with the drive or if they're all motor/pump. Drive has input and output reactors. Motor connected by VFD cable which is about 100 feet long. Motor termination is by copper split bolts.
First thing we noticed was that the drive doesn't give the typical VFD whirr noise when running, it just sounds off. This persists even when changing carrier frequency from min to max. Someone decided to leave it at 2kHz. The motor and drive do not get hotter than normal as far as we can tell.
Last year one of the motor-side leads melted inside of the motor junction box. I think it's possible the split bolt terminal was loose, but the motor might have been on its way out considering that a couple months later the motor shorted to ground and we had to get it rebuilt. I don't remember if it was the same phase as the melted wire.
Fast forward 6 months, drive tripped on ground short circuit. I changed carrier frequency to 4kHz according to the manual and double checked all parameters. Then I ran it again and it tripped after 5 minutes. I megged the VFD cable on both sides, megged the motor, and used two different meggers to be sure. I turned the motor shaft by hand and let it spin while I megged the motor. Had the guys who rebuilt our motor send out a tech with a fancy tester to check the windings and insulation. Everything checked out. Re-wrapped the split bolts and put it back in service. Ran for 2 weeks and got another ground short fault. Reset, ran a few days then a motor short fault. Megged everything again, no indication of failure. Put it back in service and it faulted again a few days later.
I've done some searching online for others who have had similar issues. I see people talking about electrical noise, pinholes in wire insulation, heat expansion, and motor vibration. The last one sounds convincing, like the pump is unbalanced or something, considering all the previous issues we've been having and I'd love to know a good (and preferably inexpensive) instrument I can use to log vibration, and if anyone has some pointers on a guide for checking, selecting equipment, peak vs rms etc.
In the meantime we just got a Fluke MDA-550 drive analyzer and once I figure out how to use it, I am going to use it to record the drive. I'm super pressed for time with other projects, so would it be fruitful to check with AND without load on the output and DC bus (4 tests total), or can I save time by checking it just one way or another?