I haven't been there yet. Monday
Old ATV11HU4 drive. Single phase in three out. Rated 3 HP out.
It has been working on an existing dough mixer of 1.5 HP.
The area EC tried connecting it to a larger, new to customer, mixer of 2.5 HP. It trips the 30 amp GE breaker and displays a fault of "SCF". Short Circuit to motor.
FWIU, they are using it as phase conversion, and star/stop the mixer(s) via its ATL contactors. Would the HP change be enough to change the response of the VFD to the cycling load contactor?
I guess I'm surprised it blew the breaker vs shut down the drive on the fault.
They connected it back to the smaller mixer and it still works.
Monday.