The purples are about the best I have found. I didn't know there was a barrel connector made for copper to alum. I have never used them. Interestingly enough, I have been told that there is not a wire connector out there that is rated for alum to alum. The purples are rated copper to alum, not alum to alum.
I always thought if connectors were rated Cu/Al, that meant they could connect Cu to Cu, Cu to Al, or Al to Al. Is that not correct?The purples are about the best I have found. I didn't know there was a barrel connector made for copper to alum. I have never used them. Interestingly enough, I have been told that there is not a wire connector out there that is rated for alum to alum. The purples are rated copper to alum, not alum to alum.
If they have separate termination points (screws for example) for the two wires, like the purple whose photo was posted, and they are not separately labelled, you can certainly put two Cu, two Al or either combination into those termination points.I always thought if connectors were rated Cu/Al, that meant they could connect Cu to Cu, Cu to Al, or Al to Al. Is that not correct?
If it is a wire nut which applies force to both conductors at the same time or a termination rated for two wires in one opening, it might not work as well for Al to Al as for Cu to Cu, and might not be tested for all combinations.
When in doubt, look at the instructions and not just the product name. On a switch or receptacle, Cu/Al means that each individual termination point can accept either Cu or Al, but you will not be dealing with the situation of two conductors under one screw or one pressure plate. (I have used a combo USB/120 receptacle (Pass & Seymour freebie) which for space reasons provides only one screw for hot and one for neutral, but has two wire slots going under each pressure plate so that you can still extend the wiring without using a pigtail. That unit was not rated for Cu/Al though.)
When in doubt, look at the instructions and not just the product name. On a switch or receptacle, Cu/Al means that each individual termination point can accept either Cu or Al, but you will not be dealing with the situation of two conductors under one screw or one pressure plate. (I have used a combo USB/120 receptacle which for space reasons provides only one screw for hot and one for neutral, but has two wire slots going under each pressure plate so that you can still extend the wiring without using a pigtail. That unit was not rated for Cu/Al though.)
Duly noted, and each port can accept either one Al or one Cu in the listed size range. My references to two or three wires were for other devices.I would just like to say that the alumiconns are only listed for 1 wire per port
Here is one:
http://www.kinginnovation.com/products/alumiconn/alumiconn-2-port/
Fill out the form on the page and get a free sample.
Read Jesse Aronstein's paper.... I guess you can put a short piece of 14 copper in there and cap the end.
It is dated, and does not necessarily apply to any or all current Al/Cu connectors when used for Al-Al, but the principle is there.- The Ideal #65 connector does not consistently pass the UL "heat-cycle" test requirement when tested with aluminum wire of the type actually
installed in homes with current passing through the aluminum-aluminum path in a pigtailing (aluminum-aluminum-copper) splice.
With field supplied tape or shrink wrap, I presume.These are rated for Al & Cu. I use them a lot for splices. They are made by Ideal.
Here is one:
You can try this COPALUM crimp method. http://www.te.com/catalog/cinf/en/c/10914/968
Watch this You Tube video http://www.youtube.com/watch?v=x920gPEkWhQ
One of the contractors in my Association rents the crimp tool on a monthly basis.