Aluminum alloys

Status
Not open for further replies.

paul32

Senior Member
Location
Minnesota
I'm trying to understand the real risk of using aluminum today, and conflicting and confusing information doesn't help. I have lots of questions and am not sure where to start.

I have gathered the old aluminum that caused all the problems was AA-1350, and the "new" stuff created in the 70s is the AA-8000 series. Also, I couldn't find the thread, but someone (iwire maybe) once made a comment that larger sizes of wire never had a problem. If so, what is considered the larger sizes. Did 8AWG connections for 30A dryers with the old aluminum have problems?

For the larger sizes, say 2AWG and larger for services, do people use antioxidant for all aluminum or just the old 1350. I find it odd the UL says it is based on the recommendation of the connector. Also, I think they say copper and aluminum are the same, which makes even less sense since aluminum oxide is a poor conductor compared with copper oxide. Someone said the 8000 series doesn't oxidize (one site I found says otherwise), which if true would also say applying antioxidant should be based on the wire and not the connector.

I hear that the 8000 series is just as good as copper, which again I don't believe with aluminum oxide being a poor conductor. If the statement is really 8000 series installed with antioxidant is as good as copper, I might accept that. But I also hear copper is more forgiving for a bad installation. That to me says copper is better. If an installation could be measured, a higher level is needed for aluminum to be acceptable. What is needed to make the installation of aluminum as good as typical copper installation (for a service lateral)?

I torque all my connections in a panel now, even the 14AWG. I always wonder how accurate does the torque need to be. One way that copper could be more forgiving is the torque spec is wider (I don't know what it is). If a lug says 50 in-lb, what is the real range of being a good permanent connection, both for copper and aluminum? Part of my concern is how accurate is the torque wrench being used. Just specifying 50 in-lb as a spec doesn't cut it, unless it is a minimum (which I don't think it is), since it is impossible to torque it to EXACTLY 50 in-lb.

Another thing, even if we can say the 8000 series aluminum is great and fixes the past problems, I find my suppliers only carry a few sizes that are 8000 series. I was surprised to find 1350 is not only readily available, it is the only thing available for some sizes. Related to this is the code doesn't say USE, RHH, and others have to the 8000 series. Does anyone know why it only requires it for certain insulations (and small conductors nobody makes :) )?
 
I guess this would happen.

I guess this would happen.

With the price of copper going up as it did before, once again aluminum it is being considered a potential substitute for copper.
 
Paul,

I think a review of aluminum use is definitely in order, given the cost of copper right now.

2005 NEC and Handbook commentary
310.14 Aluminum Conductor Material
Solid aluminum conductors 8, 10, and 12 AWG shall be made of an AA-8000 series electrical grade aluminum alloy conductor material. Stranded aluminum conductors 8 AWG through 1000 kcmil marked as Type RHH, RHW, XHHW, THW, THHW, THWN, THHN, service-entrance Type SE Style U and SE Style R shall be made of an AA-8000 series electrical grade aluminum alloy conductor material.


Section 310.14 provides proper recognition of approved AA-8000 series electrical-grade aluminum alloy conductor materials for wire and cable products. It also provides coordination with the UL listing requirements for testing terminations, such as CO/ALR devices and other connectors, suitable for use with aluminum conductors. The electrical industry has developed AA-8000 series aluminum alloy materials and the connectors suitable for use with aluminum conductors to provide for safe and stable connections. Connections suitable for use with aluminum conductors are also generally listed as suitable for use with copper conductors and are marked accordingly, such as AL7CU or AL9CU. Numbers 7 and 9 identify the temperature ratings of 75?C and 90?C, respectively, for these connectors.
When I read 310.14, it seems clear that regardless of whether a supplier stocks RHH or USE in AA8000, I am required to install AA8000.
 
We have installed several 2000 to 4000 amp services with series 8000 aluminum wire. We use penetrox on the terminations. The engineers and inspectors tell us that the properties of the series 8000 aluminum are really close to copper.
When you have a service that would cost $40,000 using copper and can use the aluminum at $14,000 it makes sense to install it.
I just hope this is not like the Quest water conduit thing and 10 years down the road services start blowing up !!!
I am the proud recipitent of some money from the Quest class action lawsuit of the 80's. I think after all the busted water lines I repaired I recieved a check for $3.26 for my part of the lawsuit. I went out and took myself to McDonald's and have a happy meal.
 
2005 NEC and Handbook commentary
310.14 Aluminum Conductor Material
Solid aluminum conductors 8, 10, and 12 AWG shall be made of an AA-8000 series electrical grade aluminum alloy conductor material. Stranded aluminum conductors 8 AWG through 1000 kcmil marked as Type RHH, RHW, XHHW, THW, THHW, THWN, THHN, service-entrance Type SE Style U and SE Style R shall be made of an AA-8000 series electrical grade aluminum alloy conductor material.

I'll highligh a different part. It isn't that all stranded conductors are to be AA-8000, all (stranded) conductors of those types must be. USE is not on the list (RHH is, I remembered wrong, but XHHW is missing).
 
I am a strong believer in ALCAN stabiloy feeders for conductors 100A and larger on projects. I have installed them on projects almost 10 years ago without any issues to date.

Currently in my recent role I budget many projects and it is about a 30% to 40% savings by using Stabiloy in EMT rather than Copper in EMT.

The attached website lists 100's of projects that have used Stabiloy conductors (The list on this website is about 5 years old) and I have just received an update from ALCAN to pass on to a couple of clients to use on upcoming projects.

http://www.cable.alcan.com/alcancable/en-US/Markets/Building+Wire/Reference+Library/

-Ed
 
dduffee260 said:
I just hope this is not like the Quest water conduit thing and 10 years down the road services start blowing up !!!
I am the proud recipitent of some money from the Quest class action lawsuit of the 80's. I think after all the busted water lines I repaired I recieved a check for $3.26 for my part of the lawsuit. I went out and took myself to McDonald's and have a happy meal.

What was the Quest water conduit thing?
 
paul32 said:
USE is not on the list (RHH is, I remembered wrong, but XHHW is missing).
service-entrance Type SE Style U is USE.

XHHW is XHHW.
 
petersonra said:
What was the Quest water conduit thing?

Back in the early to mid 80's they used gray pvc conduit for water lines called Quest. The conduit was really cheap, the fittings were really cheap also. The fittings were a small metal band applied with a squeeze tool.
Hence after about 5 to 8 years almost every line in my house leaked. I literally replaced every fitting throughout the house to remedy the leak problem. Well apparently some attorney's friend used the stuff to, so that is how the class action lawsuit got started. They since have upgraded the fittings to a compression type with a gland ring.
I see now where they are using a red and blue pvc water conduit with the same fittings. I asked the plumber how good the fittings were. He said " they say they will never leak". We will see in about 5 years if that is true.
 
The grey water pipe was polybutylene. The red and blue stuff (it also comes in white) is cross-linked polyethylene, or PEX.
 
Out here on the left coast we have been using AA-8000 AL conductors for decades with almost no problems. It is encumbant on the installer to be familiar with the products and installation techniques. Antioxident componts (if used) must be used in accordance with the manufacturers instructions. There is no requirement in either the NEC or UL white book to use the compounds unless required by the manufacturer of the connector or fitting.

Life is good,

Bob
 
al hildenbrand said:
service-entrance Type SE Style U is USE.
Al, I'm surprised to see someone as experienced as you saying that. USE and SEU are NOT the same thing! You cannot use SEU for direct burial.

XHHW is XHHW.
Oops. Read it too quick (expected XHHW to be last in alphabetical order :) ). Originally thinking RHH was missing from the list was another thread saying that I think. I'll never find it the way the new search works (RHH and USE are too short blah blah and won't be included in your search :mad: ).

In any case, anyone know the reason for the specific list of insulation types rather than saying all conductors should be AA-8000 series?
 
paul32 said:
Al, I'm surprised to see someone as experienced as you saying that. USE and SEU are NOT the same thing! You cannot use SEU for direct burial.

What is SEU and where would I find a listing for this cable?
It is not mentioned in Article 338.
 
Paul,

Take a look at the UL "White Book", TYLZ, and you'll read:
[FONT=Arial,Bold]
SERVICE ENTRANCE CABLE (TYLZ)
GENERAL



[/FONT]
This category covers service entrance cable designated Type SE and Type USE for use in accordance with Article 338 of ANSI/NFPA 70, ?National Electrical Code? (NEC).



Service entrance cable, rated 600 V, is Listed in sizes 14 AWG and larger for copper, and 12 AWG and larger for aluminum or copper-clad aluminum. Type SE cable contains Type RHW, RHW-2, XHHW, XHHW-2, THWN or THWN-2 conductors. Type USE cable contains conductors with insulation equivalent to RHW or XHHW. Type USE-2 contains insulation equivalent to RHW-2 or XHHW-2 and is rated 90?C wet or dry.​

The cable is designated as follows:​



[FONT=Arial,Bold]
Type SE
[/FONT]
? Indicates cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun.





[FONT=Arial,Bold]
Types USE and USE-2
[/FONT]
? Indicates cable for underground installation including direct burial in the earth. Cable in sizes 4/0 AWG and smaller and having all conductors insulated is suitable for all of the underground uses for which Type UF cable is permitted by the NEC. Types USE and USE-2 are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment. Both the insulation and the outer covering, when used, on single and multiconductor Types USE and USE-2, are suitable for use where exposed to sun.
 
I always thought that SE-U meant Service Entrance the Usual stuff and USE meant Underground Service Entrance
Now it gets a little funny when we talk about that SE-R cable.
This means Service Entrance cable that is round (hee?hee?hee..)
 
Paul,

You are right. USE isn't on the list, and USE is not SEU. Sorry for my confusion.

Perhaps the reason USE is not on the list is that it can't be used inside premises.
 
ed downey said:
Thanks for the link. It maybe wasn't what you were pointing me to, but this had a document of a study that compared copper and AA-8030 aluminum, and showed good results.

I still wonder about larger sizes of the old aluminum and whether it has had problems. Sites promoting AMP copalum seem to trash all aluminum, but I don't buy that. Is it true (and anyone have a reference) that the only problems have been both OLD aluminum (EC or 1350) AND wrap around screw terminals? Meaning everything with AA-8000 and even AA-1350 with set screw or compression connections have not had problems?

Also, that study mentioned using wire brush and antioxidant as proper installation, for both aluminum and copper. I don't understand the statement for copper, but it would make more sense to say it is always required rather than dependant on the lug manufacturer. I'll make a separate poll thread on this topic.
 