S smb1 Member Location richmond, va usa Apr 30, 2014 #1 What is the recommended/required interval between inpections of aluminum terminations in commercial buildings? Feeds and branch
What is the recommended/required interval between inpections of aluminum terminations in commercial buildings? Feeds and branch
T texie Senior Member Location Fort Collins, Colorado Occupation Electrician, Contractor, Inspector Apr 30, 2014 #2 smb1 said: What is the recommended/required interval between inpections of aluminum terminations in commercial buildings? Feeds and branch Click to expand... NFPA 70B covers this. It should be noted that modern day AL building wire alloys due not require (and should not be) periodic re-tightening. Here is an IAEI article that may be of interest on this subject:http://www.aluminum.org/sites/default/files/Aluminum Building Wire Installation & Terminations.pdf
smb1 said: What is the recommended/required interval between inpections of aluminum terminations in commercial buildings? Feeds and branch Click to expand... NFPA 70B covers this. It should be noted that modern day AL building wire alloys due not require (and should not be) periodic re-tightening. Here is an IAEI article that may be of interest on this subject:http://www.aluminum.org/sites/default/files/Aluminum Building Wire Installation & Terminations.pdf