got a service call today. customers electric range didnt work. went downstairs and found myself a nice lovely FPE panel. i opened the panel and found the 2 pole breaker tripped. i also found very loose connections on the breaker so i tightened them down. i turn the breaker on and checked the breaker using the FOP method. all normal no problems there.
then iturned on the oven all burners and oven on broil and then checked amperage. all normal there. then i checked the conductors with a infared thermometer and they were hot!! soon after the breaker tripped so i take the conductors off of the terminals and noticed they were all scratched up and they had an impresson from superman tightening down the terminal.
it looks like someone taken linesmen pliers and twisted them around the conductor damaging it in the process. i cut off the bad end and stripped it properly and installed it on hte breaker and the heat went away. i believe the problem was those scratched up and damaged conductor ends. everyone agree? whats everyones opinion?
then iturned on the oven all burners and oven on broil and then checked amperage. all normal there. then i checked the conductors with a infared thermometer and they were hot!! soon after the breaker tripped so i take the conductors off of the terminals and noticed they were all scratched up and they had an impresson from superman tightening down the terminal.
it looks like someone taken linesmen pliers and twisted them around the conductor damaging it in the process. i cut off the bad end and stripped it properly and installed it on hte breaker and the heat went away. i believe the problem was those scratched up and damaged conductor ends. everyone agree? whats everyones opinion?