Rigid metal conduit includes rigid aluminum conduit, so you have to look to 344.10(A)(3).IMO, that would be a corrosive area. If so:
(B) Wiring Methods. Wiring methods in the areas described in 680.14(A) shall be listed and identified for use in such areas. Rigid metal conduit, intermediate metal conduit, rigid poly vinyl chloride conduit, and reinforced thermosetting resin conduit shall be considered to be resistant to the corrosive environment specified in 680.14(A).
I absolutely agree with you, I wonder if that means that list is the only kind of conduit that can be used.IMO, that would be a corrosive area. If so:
(B) Wiring Methods. Wiring methods in the areas described in 680.14(A) shall be listed and identified for use in such areas. Rigid metal conduit, intermediate metal conduit, rigid poly vinyl chloride conduit, and reinforced thermosetting resin conduit shall be considered to be resistant to the corrosive environment specified in 680.14(A).
380.25 (b) clearly states no aluminum conduit in the poop are subject to corrosion?Rigid metal conduit includes rigid aluminum conduit, so you have to look to 344.10(A)(3).
**** Pool area lolI absolutely agree with you, I wonder if that means that list is the only kind of conduit that can be used.
380.25 (b) clearly states no aluminum conduit in the poop are subject to corrosion?
380.25 (b) clearly states no aluminum conduit in the poop are subject to corrosion?
**** Pool area lol
Simply pointing out that "rigid conduit" includes more than the typical galvanized steel conduit.I absolutely agree with you, I wonder if that means that list is the only kind of conduit that can be used.
380.25 (b) clearly states no aluminum conduit in the poop are subject to corrosion?
Its not, but based in the rules in 344 and not directly on those in 680.Ok great so if you read my original question that is what I was asking , but knowing that aluminum is not allowed for feeder circuits due to pool chemicals being corrosive to aluminum. Why would it be allowed for branch circuits??
Can you please cite the rules in 344 that prohibit this? I appreciate the help btw thanks !!Its not, but based in the rules in 344 and not directly on those in 680.
344.10 (A) and (B) to start.Can you please cite the rules in 344 that prohibit this?
680.14(A) Wiring Methods.
Wiring methods shall be suitable for use in corrosive environments. Rigid metal conduit, intermediate metal conduit, rigid polyvinyl chloride conduit, reinforced thermosetting resin conduit, and liquidtight flexible nonmetallic conduit shall be considered suitable for use. Aluminum conduit and tubing shall not be permitted.
yes, that is the second draft text for the 2023 code.That is going to be added in the 2023? I'm looking through my 2020 book right now
Nice they added tubing. EMT is not conduitsee 344.20(A)(3) in the 2017 code.
The 2023 code will more directly address this issue.
you usually end up having to use a larger size wire if it is AL so the voltage drop ends up being similar.Aluminum conduit is not permitted in the pool area because it is prone to corrosion. Aluminum conductors are not commonly used for smaller branch circuits up to about 30 amps, but they are commonly used for services, branch circuits, and feeders. The electricians always said that copper was the only option for pool pump wire material. Copper has lower resistance than aluminum, which is the other common wire material. The low resistance of copper reduces voltage drop. The more horsepower a motor has, the more electricity it requires.