Aluminum Conduit

Status
Not open for further replies.

bob

Senior Member
Location
Alabama
I seldom see AL conduit spec or discussed in this forum. Conduit is allowed to be used as an EGC.
However due to the iron in GRC or EMT or equal
the the magnetic field arising from the fault current increases the impedance of the conduit
thus limiting the lenght of the run. However the AL is not effected in the same way since it has no iron. The length of the run can be much greater and still provide a good EGC. Under what conditions other than in concrete or underground would AL conduit not be used? This subject is covered very well in the Soares Book on Grounding.
 
Re: Aluminum Conduit

The impedance of the fault path needs to be of a value to assure operation of overcurrent devices.

Any fault current more than needed is called "meltdown".

The impedance of conduit is variable in direct proportion to intensity of current.

Magnetic fields do not affect aluminum, but aluminum does not affect magnetic fields either.
 
Re: Aluminum Conduit

You have to use Al in healthcare facilities in MRI rooms. Obviously due to the magnetic field of the MRI machine.