Can i use aluminum wire for a EGC if it is 18" from the ground ( earth).
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
AL is acceptable as an EGC (250.118) or a GEC (250.64) conductor (above 18")
 

John120/240

Senior Member
Location
Olathe, Kansas
So the aluminum conductor would have to be used for a waterline ground

application, correct. I cannot imagine how you would use it for a ground rod &

maintain the proper distance from earth. It would be major hack to drive a 10 foot ground rod & leave 2 feet above grade.
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
An insulated aluminum conductor can be used as an EGC in buried raceways or as direct burial cable. The 18 inch from the earth rule is in 250.64 and applies to terminations of GEC's.
 