I believe that the conductors are copper but the jacket is Al.The device would also have to be Al rated wouldn't it?
AFAIK just regular MC would comply.I believe 210.12 requires steel armored MC
Yes, 210.12(A)(5) just says MC, so any listed MC would be permitted.AFAIK just regular MC would comply.
Not sure about later Codes but 2017:Yes, 210.12(A)(5) just says MC, so any listed MC would be permitted.
The 2023 is a bit different with steel having been removed.Not sure about later Codes but 2017:
(5) If RMC, IMC, EMT, Type MC, or steel-armored Type AC cables meeting the requirements of 250.118, metal wireways,
metal auxiliary gutters,
I mis-read and applied the "steel armor" to MC
oooppps
Note that the MC would have to either have a wire type equipment grounding conductor, or be of the newer type with the bare aluminum bonding conductor in contact with the metal sheath. That type also requires fittings that are marked “MCI-A,” or “Metal-Clad Interlocking Armored(5) If metal raceway, metal wireways, metal auxiliary gutters, or Type MC or Type AC cable meeting the applicable requirements of 250.118, with metal boxes, metal conduit bodies, and metal enclosures are installed for the portion of the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a listed outlet branch-circuit-type AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.