Boopizi
Member
- Location
- Central PA
New to the forums so i apologize if my question is in the wrong category or has been previously discussed.
My question: Is there somewhere in the code book that permits the use of an appropriate sized Aluminum wire as a main/system bonding jumper? It obviously states right in NEC 250.28(A) "Main bonding jumpers and system bonding jumpers shall be of COPPER or OTHER CORROSION-RESISTANT MATERIAL. To me that excludes Aluminum right off the bat. However I am finding other sources suggesting that only in a corrosive environment is Aluminum not permissible to use. So I must be missing something silly somewhere.
Any help is appreciated!
IAEI Magazine - "The main bonding jumper is permitted to consist of a wire, bus, screw or other suitable conductor. It must be fabricated of copper or other corrosion-resistant material. Aluminum alloys are permitted where the environment is acceptable."
My question: Is there somewhere in the code book that permits the use of an appropriate sized Aluminum wire as a main/system bonding jumper? It obviously states right in NEC 250.28(A) "Main bonding jumpers and system bonding jumpers shall be of COPPER or OTHER CORROSION-RESISTANT MATERIAL. To me that excludes Aluminum right off the bat. However I am finding other sources suggesting that only in a corrosive environment is Aluminum not permissible to use. So I must be missing something silly somewhere.
Any help is appreciated!
IAEI Magazine - "The main bonding jumper is permitted to consist of a wire, bus, screw or other suitable conductor. It must be fabricated of copper or other corrosion-resistant material. Aluminum alloys are permitted where the environment is acceptable."