Aluminum wired homes

Status
Not open for further replies.

willis t.

New member
I have a situation in a house that belongs to a friend of a friend.. Their entire house is wired with aluminum wire and they are having problems with devices not working. (loose connections) I do not have much experience with aluminum wired homes... I know replacing the entire house with copper would be ideal, but I would like to find a safe alternative... IS using the copper to aluminum wire nuts w/ noox and pig tailing everything going to do the job???
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
willis t. said:
I have a situation in a house that belongs to a friend of a friend.. Their entire house is wired with aluminum wire and they are having problems with devices not working. (loose connections) I do not have much experience with aluminum wired homes... I know replacing the entire house with copper would be ideal, but I would like to find a safe alternative... IS using the copper to aluminum wire nuts w/ noox and pig tailing everything going to do the job???

That is my preferred way of doing it. I have not had a problem with that method.
 

mdshunk

Senior Member
Location
Right here.
willis t. said:
... IS using the copper to aluminum wire nuts w/ noox and pig tailing everything going to do the job???
I can't really get on board with that, knowing what I know now. Once upon a time, I'd have said 'yes' to that. Now, I think that just replacing the devices with co/alr rated devices is probably at least as good as anything else you could do. Pigtailing with the purples causes you to jam the conductors harder back inside the box, which doesn't always work out so well with aluminium.
 

Brady Electric

Senior Member
Location
Asheville, N. C.
Aluminum wired homes

I agree with both responses only to add,be sure that in the outlets and switches you tighten down screws. (throughout the hole house)
In most houses that I have been in that have aluminum wire the screws are loose in the outlets and switches have arced and burned into.
Don't forget the breakers.
Semper Fi Buddy
 

brian john

Senior Member
Location
Leesburg, VA
I would approach it as noted BUT.

If the friend plans to stay there a long time start rewiring a room at a time.

Safer and would help with resale later.
 

barbeer

Senior Member
I own a home wired with AL and have not had a problem. I have replaced every device in the house and they all looked great, no evidence of heating.... I have added circuits with CU but that is only cause AL is not readily available and I do really prefer CU. I guess what I am trying to say is that it's not all bad.?
 

SEO

Senior Member
Location
Michigan
Aluminum wiring was popular in some areas in the mid to late 60's. Part of the problem with al when it was installed is that most installers (electricians) were not trained in proper installation practices. To my knowledge there were not any devices rated for al conductors at that time and over time there have been some problems. It can be repaired with listed fittings and devices but not knowing whats in the wall I would encourage your friend to rewire with copper if problems start to arise.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The main cause of loose connections with small-gauge aluminum is a combination of the fact that the aluminum is softer than the terminal metals, and that it has a high rate of expansion with heat.

Current flow heats up the wire, which flattens under the screw head, and removing the current allows the wire to cool. Subsequent current causes higher heat from the now-flattened wire, and it repeats.

Every time the connection heats up, it gets looser, which causes more heat. Now that the wire is flattened, a good re-tightening the terminals improves contact because of the increased contact area.
 

M. D.

Senior Member
K8MHZ said:
They don't seem to be available any longer.

Sad, they were a cold weld crimp protected by shrink tubing. Sounded like a good idea, to me.

Well I just called the electrical contractor from the link and he says they are, and that they work quite nicely,.. down side is you have to take a course lease the tool and buy the things from tyco
 

M. D.

Senior Member
The guy I talked to ,. said he thought these would be a good alternative , he has a few in his own house,.. been there two years , he checks them periodically no concerns as of yet

AlumiConn connectors and aluminum wire aluminum to copper lug connectors used for pigtailing or splicing may be observed in homes where aluminum wiring repairs have begun after about June 2007. [New in 2006, U.L. Listed, 2007 completed independent testing
 

ohm

Senior Member
Location
Birmingham, AL
A few years ago I found a receptacle running at 300 deg f. on AL wire. The downstream lights were at half brilliance. The wire and connections looked fine but tested terrible. I pigtailed to CU with lots of NOLOX and have not heard of any further problems.

I did the best I could with what I had but I admit it was not up to Code. Looking into a correct fix turned into a joke. Even UL listed devices (Ideal) are comming under fire from various agencies. The listed CU/AL receptacles cost $3 each and as Marc pointed out pigtails are a problem.
 

richxtlc

Senior Member
Location
Tampa Florida
The expansion and contaction of aluminum wire may be one cause of loose connections, the other is use of none AL or CU/AL switches, recepticals,etc.
If there are only CU switches, etc then oxidation of the aluminum wire is the problem as the aluminum acts as the anode and the copper the cathode. The aluminum becomes powdery and falls off due to normal use and becomes a loose connection.

This caused many fires when home owners replaced the switches and outlets with ones rated for CU only.
 

charlietuna

Senior Member
if you consider everything mentioned here -- i think you'd be ok to pigtail copper using rated wire nuts and being careful not to overload the junction boxes with extra wire. most problems i have come across are homes wired with aluminum branch circuits and connected to the devices using the backstabs. when a splice is made properly and not overloaded it usually will last the lifespan of the home. for re-sale? i don't think the average house inspector would catch it -- and if he does--so what it is wired to code!
 

220/221

Senior Member
Location
AZ
Aluminum wiring is not the problem.

Poor installation of aluminum wiring is the problem

I'm going to have to agree with that one.


I also think that the listed AL wire nuts are a joke/scam.

Regular nuts were fine for many years then somehow became bad??? I don't think so. There is a lot of AL wiring in tract houses here built between 72 and 76 and the only issues I ever see are due to improper devices or somebody reworking it.
 

B4T

Senior Member
AL/CU "Purple Wire Nuts"

AL/CU "Purple Wire Nuts"

The probem I found is every Electrical Inspection Agency I contacted about pigtailing won't sign-off on this option. Only COLAR devices will pass Inspection and get me a certificate. The wires in most boxes have to be stripped again to get a "clean" end. This means the wires are too short to make a loop for the device screw, so only option is to wirenut another piece of Aluminum Wire. Nothing worse than pulling the switch out of the wall and having 1 inch of wire to work with.
 

76nemo

Senior Member
Location
Ogdensburg, NY
If I mention the Ideal 61-165 again, the moderators might think I am a spammer:cool: You can measure the impedance of branch circuits with this tester. Seems like everyone here despises that tester, but to each their own. I bought that tester for this subject alone/AL wiring.

Everyone seems to think,..."Oh, that's just a little plug and play tester." No, I use the 61-183 adapter with it as well. I don't even like Ideal testing tools, not in the least, but I DO like the SureTest. It's the only thing from Ideal I own besides a CAT crimper and hand benders.
 