Aluminum Wiring Mitigating

Status
Not open for further replies.

euclid43

Senior Member
Since the problem with aluminum wiring in residential houses is at the screw down points of the devices, why wouldn't an AFCI be sufficient/acceptable to deter the fires. It detects arcing and sparking,..... so why install purple wirenuts as a deterant when they could still cause arcing and sparking without being detected, if not done correctly?
 
It appears that the most common type of failure is a glowing connection and that is not a type of fault that an AFCI can detect. It is a high resistance connection that produces excessive heat, but does not arc.
 
Ok, after seeing some of pictures where fires occurred, you would think that AFCI would be involved. I think it's better than leaving them alone.
 